I need to install a dryer and need to know, for sure, what size breaker and wire needed. FYI, the total wire run is only 10 feet.
 

·
Registered
Joined
·
698 Posts
10-3 wire with 30A double pole breaker. 2 hots (red and black) with white neutral, ground to box. Older dryers only have three prong cords--replace old cord with new one that has 4 prong (with a separate ground, older dryers grounded through the neutral...bad idea). Use a 4 prong receptacle.
 

·
de oppresso liber
Joined
·
16,879 Posts
Discussion Starter · #3 ·
10-3 wire with 30A double pole breaker. 2 hots (red and black) with white neutral, ground to box. Older dryers only have three prong cords--replace old cord with new one that has 4 prong (with a separate ground, older dryers grounded through the neutral...bad idea). Use a 4 prong receptacle.
That's what I was thinking but I wasn't sure 10 ga wire would be enough.
 