I have a portable Genrac 7550 running watt genarator. Today when I went to use the external power to run a grider , I couldn't get it to work. Took the grinder inside and it worked fine. So it must be in the portable, Any thoughts on what to do
 

·
Registered
Joined
·
9,582 Posts
Gregg Alexander said:
I have a portable Genrac 7550 running watt genarator. Today when I went to use the external power to run a grider , I couldn't get it to work. Took the grinder inside and it worked fine. So it must be in the portable, Any thoughts on what to do
............Maybe you popped a resetable circuit breaker . Maybe a single wire came loose on the backside of the panel . You should have some kind of voltage meter so test all plugins for the presence of voltage . It's also possible that you have an AVR\automatic voltage regulator that has malfunctioned . , fordy
 

·
Premium Member
Joined
·
2,567 Posts
not real likely but it may have lost it residual magnetic charge in the generator, your manual should tell you how to re set the residual magnetism, a generator should be ran ever 6 months of so to keep it there,

with out the residual magnetism in the field they can't start to generate electricity