wood stove and chimney question

We want to get a wood stove in finally. According to the chimney/wood stove guy we consulted an 8 inch flue would be best. All we can find our wood stoves with 6 inch stove pipe openings and no one can tell us if that can be sized up to an 8 inch flue or if that means we will have a 6 inch flue. Chimney guy is not available to contact right now, people at places like Lowes don't know anything about it because they don't install the stoves.

What should I be looking for in a wood stove to make it meet the chimney guy's suggestion, he says with a smaller flue we would have to have the chimney lined but with a bigger flue we won't.

We are trying to keep the cost down if possible as much as I would love a really nice looking stove like Vermont Castings they aren't in the budget. We would like a window so we can see when wood needs to be added plus I like the way fires look. It's not a necessity but I would like it.

We are looking for a bigger door opening so we won't have to split wood as small. Any suggestions?

__________________
Reply With Quote
  #2  
Old 12/30/11, 02:27 PM
 
Join Date: May 2002
Location: Saint Albans, Maine
Posts: 574

You should be able to purchase a 6 X 8 increaser/reducer that would go in the stove pipe just before it goes into the flue...

__________________

Ken In Maine
www.goatschool.com

Reply With Quote
  #3  
Old 12/30/11, 02:58 PM
Banned
 
Join Date: Jul 2010
Location: Missouri
Posts: 489

Use what you woostove manufacturer suggests. The stove is designed to draught with a certain size flue. any bigger or smaller and you will not get proper draught for the stove.

__________________
Reply With Quote
  #4  
Old 12/30/11, 03:03 PM
 
Join Date: Feb 2005
Posts: 614

Is that going to let enough heat into the chimney to keep the creosote down? I guess that is the main reason to need an 8 inch flue but I can't figure out if using the increaser will work for that.

Thanks for the help, I appreciate you taking time to respond.

__________________
Reply With Quote
  #5  
Old 12/30/11, 04:22 PM
 
Join Date: Feb 2007
Location: Wisconsin
Posts: 964

Combustion in wood is in two phases. Volatiles get boiled off, and if they aren't burn, become creosote when they condense. A good hot modern stove will add secondary air to burn these gasses, and increase the efficiency. Its one of the reasons burning green wood is so cold... the temps don't get high enough to burn the gasses, so you lose half of you potential heat. The other way to keep creosote from forming is to prevent condensation in the flue. Insulated chimney pipe will help with that. The insulation will also help with draft. If you use insulated double wall pipe, then the 8" shouldn't cause any problems, even if your stove has a 6" outlet.

Follow the stoves recommendations for diameter over the "stove guy's" suggestion. They designed it... they should know how it works.

(The second phase of combustion, btw, is the charcoal thats left.)

Michael

__________________
Reply With Quote
  #6  
Old 12/30/11, 04:30 PM
Banned
 
Join Date: Jul 2010
Location: Missouri
Posts: 489

use an insulated flue pipe and you will be fine

__________________
Reply With Quote
  #7  
Old 12/30/11, 07:06 PM
 
Join Date: Dec 2008
Location: north Alabama
Posts: 9,808

The maker knows best, as usual.

__________________

2000 mockingbirds = two kilomockingbirds

Reply With Quote
  #8  
Old 12/30/11, 07:57 PM
 
Join Date: Oct 2011
Location: North Central Kentucky
Posts: 204

An 8" flue would probably be best. You can install an adapter on a 6" stove to an 8" flue with no problems. However, if you eventually get a stove with an 8" outlet, you might have problems getting it to draw right restricting it down to a 6" flue. One of my stoves has the glass front, which I enjoy seeing the fire too.

__________________
Reply With Quote
  #9  
Old 12/30/11, 08:34 PM
 
Join Date: Jan 2010
Posts: 8,743

We used a converter for years and years with our wood stove with no problem. We bought it way back in the 80s for eleven dollars to go from a 6" stove to an 8" pipe. It's just about six or eight inches long and fits from the stove to the bigger pipe.

__________________

Let he who is without sin cast the first stone.

Reply With Quote
  #10  
Old 12/30/11, 09:15 PM
 
Join Date: Feb 2005
Posts: 614

Thanks for the advice everyone. It is much appreciated. I wanted to be sure we do the right thing so we don't have to redo it. We will be studying the manufacturers instructions to make sure we have it right.

__________________
Reply With Quote
  #11  
Old 12/30/11, 09:25 PM
So many questions
 
Join Date: Feb 2011
Location: Western Michigan
Posts: 68

If you care about such things a wood stove needs be be installed exactly as the stove manufacturer specifies to be building code compliant. Most insurance companies will not insure you if you don't get a mechanical permit and inspections.

Most stoves of recent manufacture have a plate fixed to the stove that will have important information about clearances to combustible materials (back, side, top, and bottom).

There a several new stoves that have windows in the front that are reasonably priced. Around here (Michigan) you can find them at Menards. They are more modern in design than Vermont Castings though.

I would look at used stoves if you are trying to stay within a budget. Stoves like Vermont Castings sell for thousands of dollars new but you can find them used on Craigslist for several hundred dollars.

I guess my question to you is what do you hope to accomplish with a wood stove? Are you looking to heat your entire house or just something pretty to look at. Your answer will dictate what you should be looking for in a wood stove.

__________________
Reply With Quote
  #12  
Old 12/30/11, 09:27 PM
 
Join Date: Mar 2005
Location: Bartow County, GA
Posts: 6,447

While you're at it, look at installing a Magic Heat Reclaimer or similar product. The difference in pushing heat with & without it is amazing. There's a similar product that doesn't use electricity, but I don't think it works as well.

http://www.buzzillions.com/reviews/m...eaters-reviews

__________________
Only she who attempts the absurd can achieve the impossible

Last edited by Wolf mom; 12/30/11 at 09:31 PM.
Reply With Quote
  #13  
Old 12/30/11, 10:46 PM
 
Join Date: Jun 2010
Posts: 8,176

Newer stoves need to run hotter so they use the 6" pipe, build big hot fire then damper down to conserve wood. The 8" flue cools too much, this condenses the water and creosote vapors. Might work with a bigger stove, some use 8" pipe. If it were me I would size the stove you want and need and line the flue for the best results....James

__________________
Reply With Quote
  #14  
Old 12/31/11, 10:24 AM
Cabin Fever's Avatar
NRA LifeMember since 1976
 
Join Date: May 2002
Location: Between Crosslake and Emily Minnesota
Posts: 13,423
Quote:
Originally Posted by happy@home View Post
....he says with a smaller flue we would have to have the chimney lined but with a bigger flue we won't...
Based on this comment, I assume we're talking about a concrete block chimney. I say this because there is no such thing as lining/not lining a metal chimney. A chimney block with an 8x8 opening is what one would use of a stove with a 6" flue. If the stove has a 8" flue, one uses a chimney block with a 8x12" opening. In either case, ALWAYS-ALWAYS-ALWAYS line a concrete block chimney with a clay liner!

Quote:
Originally Posted by happy@home View Post
....We are looking for a bigger door opening so we won't have to split wood as small. Any suggestions?
Chimney/flue size is dictated by the door opening area. Stoves with large door openings require a 8" flue, stoves with smaller doors require a 6" flue. The reason for this is so the stove doesn't smoke into the room when the door(s) is open. If doors were always closed on woodstoves, all any of them would need is a 6" flue.
__________________
This is the government the Founding Fathers warned us about.....
Reply With Quote
  #15  
Old 12/31/11, 12:13 PM
ET1 SS's Avatar
zone 5 - riverfrontage
 
Join Date: Oct 2005
Location: Forests of maine
Posts: 5,717

Does your home have Radiant Flooring? Or baseboards? If so you may wish to consider woodstoves that heat water. So you could then circulate heated water through your radiant floor system or baseboards.

We have radiant flooring and our woodstove heats water that circulates through our floors.

It gives direct radiant heat in the area around the stove, and it also gives warmth through out the house.



If you end up with a stove that has a 6" outlet, then you will need a 6" stove pipe. I would not try to adapt that up to 8".



Our stove-pipe is not insulated. It is single-wall pipe. We have not had any problems with creosote fires. But then we do not allow any combustibles within 3' of the stove or stove-pipe. And we have a metal roof.

__________________
http://www.mofga.org/

http://www.mofga.org/Programs/FarmAp...2/Default.aspx
Reply With Quote
  #16  
Old 12/31/11, 01:03 PM
 
Join Date: Mar 2009
Location: N AL
Posts: 2,225

I'm not sure I understand completely what the problem is? We had a 8" flue and the stovepipe was 6". Stovepipe leaves the stove, goes into a thimble through the wall and empties into the 8" flue. Is yours going straight up or sideways when it leaves the stove? Be sure to understand exactly what he's recommending. Also, be sure the flue goes far enough past the top of the house or it won't draw well.

ETA The flu was the red clay flu with chimney blocks around it.

__________________

Last edited by CarolT; 12/31/11 at 01:10 PM.
Reply With Quote
  #17  
Old 12/31/11, 01:33 PM
ET1 SS's Avatar
zone 5 - riverfrontage
 
Join Date: Oct 2005
Location: Forests of maine
Posts: 5,717
Quote:
Originally Posted by CarolT View Post
I'm not sure I understand completely what the problem is? We had a 8" flue and the stovepipe was 6". Stovepipe leaves the stove, goes into a thimble through the wall and empties into the 8" flue. Is yours going straight up or sideways when it leaves the stove? Be sure to understand exactly what he's recommending. Also, be sure the flue goes far enough past the top of the house or it won't draw well.

ETA The flu was the red clay flu with chimney blocks around it.
The output from the stove is X big, if the stove-pipe is smaller then that it may restrict draft flow.

If your stove output was 8" and you stuck a 6" stove-pipe on it, there is the possibility that the smaller stove-pipe may restrict the flow of smoke.

The closer to vertical the entire process is, combined with how long [in vertical measurement] the stove-pipe is; determine how strongly it will try to draft when it is heated.

By being 4' above the roof peak, you get the added benefit of venturi-forces pulling the exhaust out from the stove-pipe.

A 4" vertical stove-pipe can only draft a maximum of so much volume of exhaust. Whereas a 6" vertical stove-pipe can draft a higher volume of exhaust; and a 8" vertical stove-pipe can draft an even greater volume of exhaust.
__________________
http://www.mofga.org/

http://www.mofga.org/Programs/FarmAp...2/Default.aspx
Reply With Quote
  #18  
Old 12/31/11, 08:04 PM
 
Join Date: Mar 2009
Location: N AL
Posts: 2,225

Yes, but they said flu, not stove-pipe. That's what I was asking. If you vent through the wall into a flu, it's different than venting straight up through the ceiling. If you vent through the wall into the flu, there's no need to adapt from a 6" stovepipe going into the flu

__________________
Reply With Quote
  #19  
Old 12/31/11, 08:43 PM
 
Join Date: Oct 2011
Location: North Central Kentucky
Posts: 204

The main thing is to install your flue correctly and safely. That is not the place to save a few pennies, even if you do the flue this year, then get the stove next year. Plenty of advice to use a certified installer, or follow manufacturers recommendations. I tried that when I wanted to install a wood stove in my last double-wide. I ran into stuff like this over and over:

Me: "Who installed your stove and flue?"
Them: "My cousin Billy Bob"
Me: "Oh cool..thank goodness! Finally! Someone certified! Can you give me his number?"
Them: " He doesn't do it any more. But if you even need a septic system installed or gutters, let me know. I can get in touch with him."

I ended up doing it myself following the instructions that came with the flue pipe and stove. Insurance inspected, OK to go and I felt pretty good about it.

__________________
Reply With Quote
  #20  
Old 12/31/11, 09:05 PM
ET1 SS's Avatar
zone 5 - riverfrontage
 
Join Date: Oct 2005
Location: Forests of maine
Posts: 5,717
Quote:
Originally Posted by CarolT View Post
Yes, but they said flu, not stove-pipe. That's what I was asking. If you vent through the wall into a flu, it's different than venting straight up through the ceiling. If you vent through the wall into the flu, there's no need to adapt from a 6" stovepipe going into the flu
Okay what is the difference between a flue and a stove pipe?

A flue is a duct or pipe, for conveying exhaust gases from a fireplace, furnace, water heater, boiler, or generator to the outdoors. It can be is 4", 5", 6", or 8" diameters.

You may wish to connect to 45degree or 90degree elbows of piping to get the right angle you need. Before finally going straight up.
__________________
http://www.mofga.org/

http://www.mofga.org/Programs/FarmAp...2/Default.aspx
Reply With Quote
Reply



Thread Tools
Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 12:29 PM.