you did not give all specifics, how much less HP?
is the gen output of a 100 amp at 120 volts 240 volts.
I have to assume its 220 volts, 24 kilowatt output. which should be right based on the horse power rating.
takes a little less then 2 hp per 1 k of generator (Alternator) output. you can figure two to be safe.
as long as you are spinning it at the proper RPM's and not over loading it should not be a problem for the generator..
More load the harder it will be on the PTO and Engine.
if it where me I would figure the safe zone, and install a appropriate breaker between the head and the load. that way your guaranteed you wont exceed it.
say you go with 24 hp = 12k x .20% =(12k - 2,400 watts) 9,600 watt safety range.
9,600 / 240 = 40 amps. you can get either a 220v/40amp breaker or two 220v/20 amp breakers. either way the breakers will not let more then that 9,600 watts pass.
|