The design idea, as already pointed out, seems much better for this outdoor boiler compared to others. The main part that makes this system work better is the remote storage tank (which any outdoor type wood boiler system should have and most don't). Keeping the water jacket temperature high and firing the boiler at higher temperatures is a step toward higher efficiencies and better operation (as mentioned).
Tank Sizing Example (better to get an experienced installer to help with this)
For example, useable water 1,000 gal x .70 (assume 70% useable hot water) = 700 gal, temperature drop 180 - 100 (maybe too low for some heating applications - verify) = 80 F degrees, heat available = 1.0 BTU/F*lb x 700 gal x 8.345 lb/gal x 80 F = 467,320 BTU stored.
If your house heat loss (at the outdoor temperature that you are investigating usually "1% ASHRAE Design Winter Temperature") is 50,000 Btu/Hr then divide this into the storage tank volume to find out how long you can go without adding more heat (wood). 467,320 BTU/50,000 BTU/Hr = 9.4 Hrs.
Good luck.
Alex
Heat Loss at Other Outdoor Temperatures
btw, if you calculate your heat loss at a design temperature and want to know the heat loss at other temperatures, the heat loss is directly proportional to the temperature difference between the outside and the inside. So you can figure your HL at any outside temperature easily.