I have a air compressor that I bought at the sale. It has a motor that blew out my switches in the house, so I bought a plug the same as my welder. When I plugged it into that, it threw the breaker quicker than the welder. It is the type that has one wheel inbetween 2 tanks. The breaker out there was a 30amp. I thought that was about the biggest there is. Any thoughts.
|
Electrical stuff is kinda complicated to do it right, and has a lot of little details that are important.
You blew out switches in the house????? (Do you mean fuses/ breakers???)
You bought a welder plug to put on the compressor. (You haven't said it was a 120, 240, or 3phase compressor - all are common, what do you have???? Was the welder a 120 or 240 welder? Not nearly enough info!)
Common breakers are 15, 20, 30, 40, 50, 60, 100, and 200. There are others.
These breakers do _NOT_ protect your compressor or your welder. The breaker protects the wire running through the walls. The breaker is sized to what the wires can handle.
Often it is real nice to have breaker that also is sized to the device you have plugged into it; but the breaker is really there to protect the wires from melting.
We need a lot more info to understand the problem. Look at the plate on the motor and tell us the phase (1 or 3) and the voltage (common for 120 or 240 to be possible on small/mid sized motors, then you have to look at the way the wires are connected inside the box). What hp is it, so we get an idea of what size we are talking about. 5hp would be about 30 amp.
I'm sure you are working on this right; but with the info you supplied, it's kinda scary what you could actually be doing wrong!

Be safe.
--->Paul