If I were called in as an electrician for this job (which I have been plenty of times) I would not be surprised to see the red wire.
If there had been a fan with a light on the ceiling or just the light, and a single switch, someone planned ahead.
I would expect to see black, red, white, and copper in the ceiling and in the switchbox.
Black w/white stripe is the light (99% probability).
I would look inside the switchbox. If I found the 3-wire (black, red, white and ground), I would expect to see one of two situations. Red left unconnected, with the black connected to the switch...or....black and red nutted together to a pigtail, with the pigtail connected to the switch. If the later, I know the other black connected to the switch is power in.
If the former, I would heat up the red and test it at the ceiling to verify the continuity. If good, and I was limited to the single switch, I would do the later as stated above. Then connect the black to black, red to black w/stripe, and the rest at the fan.
I might install an over/under switch. Connect power to the switch, black to one sw, red to the other sw. Seperate fan and light switches. same as above for the fan.
pretty common setup.
|