Sounds like it is stuck open. Check on the side of the zone valve, should be a "manual" lever to open or close it. Most valves are made to fail in the open position.
This will give you temp control for now.
Next check voltage at the T-stat with a volt meter, should show 24 volts across the t-stat leads when turned down (50 degrees) or "open", nothing when turned up (80 degrees) or "closed".
If you do have voltage, then it could be a broken wire at the t-stat, transformer, bad motor on valve, lots of things. Some valves, you can replace just the motor, some not.
This might be a big job, depending on the install.
Does it have manual valves on either side if the zone valve?
Might have to drain the boiler to replace it, if you can't isolate the zone valve.
Unscrew or unsolder the valve and replace it.