First, do what Jim-MI said--proper grounds and bonding of all equipment. I have also grounded my wind generator tower with grounding rods driven into the ground at the bottom of the 5 foot deep holes for the legs, plus more at ground level, but the generator windings aren't tied to the grounds of the tower. My PV systems have the frames tied to the racks or mountings, and then those are grounded as closely as possible to the racks. Again, I don't tie the PVs electrically to the grounds at the racks. I also have lightning arrestors at the windgenerator where the wires go underground to head for the house, and at the similar point at each PV array, plus arrestors on the DC lines coming into the house. We had a close strike by lightning a few years ago and it wrecked a circuit board on the inverter on the AC side of the inverter, so after having the inverter repaired, I added a lightning arrestor on the AC side of the inverter, too. I think I have at least 7 lightning arrestors on my system, but I may be forgetting one somewhere.
|