Breaker Tripping on Long 10-2 Run

Earlier this season, I made a rookie mistake. I was running 120v down to one of our fields to install a Gallagher M600 Fence Charger. It was a 500 foot run and I didn't know about voltage drop, so I used 14-2 and of course buried it and of course found it was WAY to small for that run.

I just redid it based on my licensed electrician buddy's advice using a continuous run of 10-2 UF romex on a 20 amp circuit. I double checked with the guy at the electric supply house and he said I was good to go.

The Breaker is still tripping!!!! I have the hot running to the breaker and the neutral and ground running to the ground bus. This is the main service panel. This is a simple run from the panel to an outlet. If the 10-2 is too small after double verifying this, I am going to go through the roof. Please, any ideas?
Reply With Quote
  #2  
Old 08/17/10, 12:18 PM
Travis in Louisiana's Avatar
Clinton, Louisiana
 
Join Date: May 2002
Location: Louisiana
Posts: 1,688
The rule of thumb is, for every 100 foot, you raise the wire size to avoid voltage drop. How much does the charger pull in amps? Does the breaker trip instantly or over a little time? If instantly, you may have a short somewhere. If over time, you may have a voltage drop, thus causing the current or amps to go high. Do you have an amp meter to check the amps with the charger on, if it takes a while before it trips? Just my two cents. Travis
__________________
Life......Is What You Make Of It
Reply With Quote
  #3  
Old 08/17/10, 12:27 PM
idahodave's Avatar  
Join Date: Jan 2005
Location: SE Idaho
Posts: 532
If it's a ground fault breaker (GFI) the neutral (white) must return to the breaker.

If it's a regular breaker, does it blow without anything plugged in? Shorted wire if it does.

Does the charger work in another outlet?
Reply With Quote
  #4  
Old 08/17/10, 12:30 PM
 
Join Date: May 2003
Posts: 100
Hello- its not a GFI. It is tripping with nothing plugged in. How is a short possible on a direct run of brand new heavy duty buriable romex?
Reply With Quote
  #5  
Old 08/17/10, 12:42 PM
Travis in Louisiana's Avatar
Clinton, Louisiana
 
Join Date: May 2002
Location: Louisiana
Posts: 1,688
First of all, I have bought brand new breakers and they would be bad. If it is tripping with nothing plugged in, then there is a short somewhere. If you have a ohm meter, disconnect all wires from the power panel, so it will not have any power on it. Also, make sure the wires on the charger end are disconnected and are not touching. Now take the ohm meter and check from the black wire to the white, then the black to the bare ground. There should be alot of resistance between the wires. If you show zero ohms or no resistance , then you have a short in the wire. Hope this helps.
__________________
Life......Is What You Make Of It
Reply With Quote
  #6  
Old 08/17/10, 12:48 PM
Travis in Louisiana's Avatar
Clinton, Louisiana
 
Join Date: May 2002
Location: Louisiana
Posts: 1,688
If you have put a recepticle at the charger end, you may have some wires touching in there causing a short.
__________________
Life......Is What You Make Of It
Reply With Quote
  #7  
Old 08/17/10, 01:10 PM
idahodave's Avatar  
Join Date: Jan 2005
Location: SE Idaho
Posts: 532
How big is the breaker (amps) and did you try another?
Reply With Quote
  #8  
Old 08/17/10, 01:32 PM
 
Join Date: May 2003
Posts: 100
Hello- Idiot here... In my haste to rewire I connected hot and neutral to the silver terminals in the outlet. Just fixed it. A-OK!
Reply With Quote
  #9  
Old 08/17/10, 01:56 PM
idahodave's Avatar  
Join Date: Jan 2005
Location: SE Idaho
Posts: 532
Good catch...glad it was a simple thing

Dave
Reply With Quote
Reply




Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 02:23 PM.
Contact Us - Homesteading Today - Archive - Privacy Statement - Top - ©Carbon Media Group Agriculture