You need a 24 volt AC door bell transformer or equivalent transformer rated at 1/2 amp or higher and a small relay with a 24 volt AC coil rated less than 1/2 amp or less. The relay points need to be rated at approximately 5 amps at 120 volts AC. Ebay has some transformers and relays.
From your 120 Volt house supply, connect the door bell transformer primary side to the 120 volt AC. Then connect the secondary with one wire to the humidistat switch and the other wire to one side of the relay coil. From the humidistat switch run a second wire to the relay coil so that when the humidistat trips to turn on the coil is activated. Each time the humidistat trips on the relay points will close.
Wire the humidifier into the relay just as you earlier described as to how you had planned to do the humidistat.
Now with the system setup in this manner when the humidistat activates, the coil on the relay will connect the points closed on the relay. The relay points can easily carry the amperage and will turn the humidifier on. When the humidistat turns off the coil voltage to the relay will cease and the relay points will open and the humidifier will turn off. This arrangement should give long service as it can handle the amperage for both the start and run conditions of the humidifier.