Angry Voltage regulation

Let's start with a little background. Two days ago during an extended power interuption I started my 3 cyl. hatz deisel, 16,000 watt 64 amp generator to power up my water pump and water circulators on the farm. All seemed fine at first, a little bit of pulse to the light bulb but nothing unusual. Then I smelled smoke, assuming it was from the generator, thought nothing of it. Until I realized it was not the smell of deisel fumes but something much worse, burning electrical wires. When I got to the water room the 100w light bulb looked like it was a 300w bulb and smoke was curling out of the 220v water circulator. I got one circulator shut down but by the time I reached the second water room the second was toast. End result, two burnt out water circulators totaling $3000.00 I am assuming it is a problem with the voltage regulator but in fact I have no idea. I would love to hear any suggestions all of you might have. Thanks
Reply With Quote
  #2  
Old 10/25/07, 07:10 PM
 
Join Date: May 2002
Posts: 7,883
Certainly sounds like your idea is right.

I keep touting about cheap generators and their pee poor voltage regulation . . . . .ending up costing far more bucks for the damage that can and will happen.

I am not at all aware of the unit you have . . . .is it a chinn-nee's unit . . . . ?

Was that the first time you had run the unit...?
Could well be that 220 was being applied to a "120" circuit.
Who wired the thing...??
Was it not tested when first installed . .?

Sorry for your loss.......
Reply With Quote
  #3  
Old 11/04/07, 09:01 PM
hotzcatz's Avatar  
Join Date: Oct 2007
Location: Hawaii
Posts: 2,854
If you divide the watts by amps you get the voltage. So it is a 250 volt generator.
Reply With Quote
Reply



Thread Tools
Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -5. The time now is 03:56 PM.
Contact Us - Homesteading Today - Archive - Privacy Statement - Top - ©Carbon Media Group Agriculture